I’ve read multiple topics and the docs, but I can’t get an output value from a Logo 8 in IPS.
The connection is there, but I can’t seem to get a changing value in IPS.
If you want the outputs, can you try using the reserved output bytes instead of data blocks? 1064 looks quite high to me. And the area address is always 0, your V address goes into the address field below the data type.
Try Outputs, 0, byte, 0, read only. Those are your first 8 outputs.